NEC 700.10(D) - fire protection

Status
Not open for further replies.

anbm

Senior Member
Location
TX
Occupation
Designer
NEC 700.10(D) requires two hour forr rated protection for emergency feeder in Assembly occupancies for not less than 1,000 persons. If the building has a mix of Assembly and other occupancy type for a total of 1,300 plus persons while Assembly space is only 740. Do we need to comply with above rule?
 

anbm

Senior Member
Location
TX
Occupation
Designer
I would say no but does anyone against/ has different thought??? Does AHJ need to make a call on this?
 