Currently working on the design of a project that will require an emergency generator. Exterior, diesel.
I believe I have loads that fall beneath each of these systems:
NEC 701 Loads: Mechanical ventilation equipment for a hazardous space Class 1 Div I. (required per IBC 414) ("Standby Power" per the IBC).
NEC 702 Loads: Boiler loads serving both bldg heating and Owner equipment loads. I consider 702 Optional loads.
In my research, and in speaking with a State electrical inspector, it is my understanding that a 701 and a 702 can be served from the same automatic transfer switch. Do you believe this is accurate?
NEC 700 to serve egress illumination requirements. This system would require its own ATS.
So.... a total of (2) ATS for the project.
ATS #1 to serve NEC 700
ATS #2 to serve NEC 701 and 702
I believe I have loads that fall beneath each of these systems:
NEC 701 Loads: Mechanical ventilation equipment for a hazardous space Class 1 Div I. (required per IBC 414) ("Standby Power" per the IBC).
NEC 702 Loads: Boiler loads serving both bldg heating and Owner equipment loads. I consider 702 Optional loads.
In my research, and in speaking with a State electrical inspector, it is my understanding that a 701 and a 702 can be served from the same automatic transfer switch. Do you believe this is accurate?
NEC 700 to serve egress illumination requirements. This system would require its own ATS.
So.... a total of (2) ATS for the project.
ATS #1 to serve NEC 700
ATS #2 to serve NEC 701 and 702