Per NEC 702.6 can key interlocks be used or are they accepted on an MCC main tie main to prevent parraleling?
stickboy1375 said:Most interlock kits are UL listed so I would say yes they are fine to install and meet the requirements of 702.6
kfenn22 said:I'm not sure why you want to use a key interlock in stead of the MTS?
usinmentor said:Per NEC 702.6 can key interlocks be used or are they accepted on an MCC main tie main to prevent parraleling?
iwire said:Its not what your thinking about.
I believe he is talking about a "Kirk Key" system.
For this application you would have 1 key, you would place a heavy duty lock on the two breakers that can not be closed at the same time.
The key is can only be removed from the lock if the breaker is locked open, so you can not close the second breaker before opening, locking, removing the key and now unlock the second breaker.
Much less expensive, just add the locks to the existing gear.
I think so, but I bet you can find out for sure at Kirk Key
There is a ton of info on that site.
bphgravity said:Check with your local AHJ. I am aware of several that look for UL-1008 listing for transfer switches and will not approve Kirk Keys.
weressl said:Then they abuse their power.
iwire said:Something we agree on ... I am going to mark this on my calender. :grin:
weressl said:Sooo?! Stop being so contrary
iwire said:I know, I have to work on that. :grin: :grin: