electricallyminded
New member
- Location
- Oakland, CA
I am looking to add a battery backup system to my home and have been confronted with standby generator sizing requirements from NEC 702. I am looking to backup the whole home which is a 200A service containing a 20A solar system. Realistically we peak at about 7 kW of demand when the dryer is turned on, usual demand is limited to no more than 3 kW otherwise.
The backup system I am looking to add provides for 5 kW of continuous power. This would seem to be not permissible per the NEC 702 sizing guidelines which reference Art 220. What is the logic behind this? I believe in this instance if the 5 kW generating capacity is exceeded that the frequency would simply collapse and I would be back where I started - in a power outage. Why is this not a permissible scenario? What is the safety risk? Any thoughts on how to overcome this besides fudging load data?
Thanks!
The backup system I am looking to add provides for 5 kW of continuous power. This would seem to be not permissible per the NEC 702 sizing guidelines which reference Art 220. What is the logic behind this? I believe in this instance if the 5 kW generating capacity is exceeded that the frequency would simply collapse and I would be back where I started - in a power outage. Why is this not a permissible scenario? What is the safety risk? Any thoughts on how to overcome this besides fudging load data?