Can someone confirm that this code applies to optional standby generators?
This is stating that the conductor and OCPD have to be sized for not less than 125% of max current rating of source.
If so, A 200A generators conductors and OCPD have to be sized to carry a minimum of 250A.
Lets walk down a hypothetical situation..
If someone oversizes the two to 400A, Loads are added later on, utility loses power, 400A rated ATS transfers 300A metered load to gen power. The conductors and OCPD wouldnt trip but...
Would the gen sense over 100% load is being pulled and turn off?
Would it essentially attempt to overload its self at 150% and heat up until it grenades it self?
Or would it essentially only output the designed 200A and something similar to a brownout would occur to the critical loads?