There is a building that has cogenerator (CHP), upon loss of power to utility should it comply with 705.40 and 705.42?
What really is the difference between 705.40 and 705.42?
705.40 tells you that if you lose primary power source, that all the electric power production sources shall be automatically disconnected and shall not be reconnected until primary source is restored. Does this also apply to 3-phase systems?
705.42 tells us something a little different regarding to 3 phase systems.
705.42 tells you that if one of the 3 phases opens (not sure if opens means loss of utility power), the power production source shall be automatically disconnected.
Unlike 705.40, why doesn't 705.42 tell you that you cannot re-connect the power production source after it being automatically disconnected? In other words, are you allowed to reconnect the power production source after it's automatically disconnected even though the utility power is still off?
What really is the difference between 705.40 and 705.42?
705.40 tells you that if you lose primary power source, that all the electric power production sources shall be automatically disconnected and shall not be reconnected until primary source is restored. Does this also apply to 3-phase systems?
705.42 tells us something a little different regarding to 3 phase systems.
705.42 tells you that if one of the 3 phases opens (not sure if opens means loss of utility power), the power production source shall be automatically disconnected.
Unlike 705.40, why doesn't 705.42 tell you that you cannot re-connect the power production source after it being automatically disconnected? In other words, are you allowed to reconnect the power production source after it's automatically disconnected even though the utility power is still off?