lenz- Per your PM I think your question is:
Is the 120V power wiring to a Fire Alarm Panel with a PLFA power supply (24VDC with battery) considered part of the Fire Alarm Circuit?
If it is part of the FA circuit, it can't be in a raceway with non-FA power conductors.
If it is not a FA circuit per the definition of "Fire Alarm Circuit", it can share araceway with other power conductors.
I think this is how your installation is put together:
120V power from a UPS panel to a local Fire Alarm panel with a listed, integra,l 24VDC, PLFA power supply + battery.
The local sensing/alarm devices are wired to the local FA panel with PLFA cables in dedicated raceways.
An alarm signal from this local FA Panel to the plant's Main FA Panel is in dedicated raceway using NPLFA/PLFA rated cable. Circuit is considered as PLFA.
Per 760.136, the 120V power cable can't go in the PLFA raceway back to the Main Panel area.
760.127 "Wiring Methods on Supply Side of the PLFA" says it has to be installed per Part II.
Part II, 760.48 (B) says "Power-supply and fire alarm circuit conductors shall be permitted in the same.....raceway only where connected to the same equipment. " Unrelated power circuits are not allowed with fire alarm circuits.
The definition of Fire Alarm Circuit includes the "portion of the wiring system between the load side of the overcurrent device or the power-limited power supply?."
I think the 120 V power is not part of the Fire Alarm Circuit because it is on the supply side of the power limited power supply. The FA circuit starts at the power supply load terminals per the "or" in the definition.
If my interpretation is correct, the dedicated 120V power cable could share a conduit with non-FA power circuits. I don't think it would diminish the integrity of the FA circuit. If the 120V circuit fails for any reason, the battery back up takes over and the trouble alarm goes off.
Could the Fire Alarm experts weigh in and tell us if my interpretation is correct or faulty?
Thanks,