NEC 760.139

Status
Not open for further replies.

wyboy

Senior Member
NEC 760.139 seems to state that power limited fire alarm conductors may be installed in the same race way with other wiring not related to the fire alarm system, specifically: Low-Powered Network-powered Broadband communication circuits, class 3 circuits and class 2 circuits meeting the requirements of NEC 760.139(B). Am I reading this correctly? I always thought fire alarm circuits must be kept separate.
 
NEC 760.139 seems to state that power limited fire alarm conductors may be installed in the same race way with other wiring not related to the fire alarm system, specifically: Low-Powered Network-powered Broadband communication circuits, class 3 circuits and class 2 circuits meeting the requirements of NEC 760.139(B). Am I reading this correctly? I always thought fire alarm circuits must be kept separate.

I was also surprised to learn this but I run into both fire and security conductors in the same conduits at every Lowes I have worked on.
 