I have a project that we are installing (40) CMP rated Data Cables (horizontal cabling) for workstations but they terminate on a lower level in the building. To get to this level, we need to run (exposed) in a Riser shaft (no conduit provided).
800.53(B)(1) only mentions CMR in the vertical shafts.
800.53(G) indicates that subsitiutions are allowed per the table (CMP is acceptable for CMR requirements).
**Am I correct that these substitutions apply to and are acceptable anywhere in the building???**
What would prevent me from installing exposed CMP rated cable in a fire rated Riser if we firestop the penetrations as required?