In the recent days I experience an argument with my Building official who claims that wire sizing & NEC can’t enforce OCPD caused by voltage drops. His quote:
"Due to it being a fine print note voltage drops are not enforceable"
My answer to his statement was:
"Boss,
If a contractor to size and run wires based only on allowable ampacities of conductors without considering voltage drops required by table 8 in Chapter 9 or 310.15(B)(2)(a), a fire will inevitably occur. For example: An entire parking lot of lights of a shopping center could be run on #14 or #12 AWG wires, and it would instantly cause a fire.
The calculation assumes uncoated copper or aluminum conductors operating at the temperature selected and is based on the ac/dc resistance or impedance from NEC 2005 Tables 8 and 9 for stranded conductors operating on a DC or AC 60Hz system. The ampacity of each conductor size in the dropdown menu below is based on NEC 2005 Table 310.16 for 60C insulated conductors rated 0 through 2000 volts with not more than three current carrying conductors in raceway, cable or earth with an ambient of 30C (86F).
Voltage drop for ac systems should total no more than 5% under full load conditions. Drops may be significantly larger during surge or motor starting conditions -- sometimes in the 15% to 25% range if other devices on the system can withstand this momentary dip. Voltage drop for DC systems should be designed as low as possible or less than 2%.
Section 90.5 (C) page 6 of the NEC states…”Footnotes to tables, although also in fine print, are NOT explanatory material unless they are identified by the abbreviation FPN. Table footnotes are part of the table and are necessary for proper use of the tables.”
BO's response:
So you are saying that the electrical code requires conformance to the voltage drop FPN?
Please help me out with suggestion or explanation that he will understand.
Thank you
Adam K
"Due to it being a fine print note voltage drops are not enforceable"
My answer to his statement was:
"Boss,
If a contractor to size and run wires based only on allowable ampacities of conductors without considering voltage drops required by table 8 in Chapter 9 or 310.15(B)(2)(a), a fire will inevitably occur. For example: An entire parking lot of lights of a shopping center could be run on #14 or #12 AWG wires, and it would instantly cause a fire.
The calculation assumes uncoated copper or aluminum conductors operating at the temperature selected and is based on the ac/dc resistance or impedance from NEC 2005 Tables 8 and 9 for stranded conductors operating on a DC or AC 60Hz system. The ampacity of each conductor size in the dropdown menu below is based on NEC 2005 Table 310.16 for 60C insulated conductors rated 0 through 2000 volts with not more than three current carrying conductors in raceway, cable or earth with an ambient of 30C (86F).
Voltage drop for ac systems should total no more than 5% under full load conditions. Drops may be significantly larger during surge or motor starting conditions -- sometimes in the 15% to 25% range if other devices on the system can withstand this momentary dip. Voltage drop for DC systems should be designed as low as possible or less than 2%.
Section 90.5 (C) page 6 of the NEC states…”Footnotes to tables, although also in fine print, are NOT explanatory material unless they are identified by the abbreviation FPN. Table footnotes are part of the table and are necessary for proper use of the tables.”
BO's response:
So you are saying that the electrical code requires conformance to the voltage drop FPN?
Please help me out with suggestion or explanation that he will understand.