stanrat said:Mike: Why is this underground duct bank stuff here if 310.15(C) says that I can use 310.16 for ampacities or calculate it?
stan
Take a look at the top of that table. It restricts its own use to a particular set of installation configurations. An underground ductbank that has three current-carrying conductors in close proximity to three others, and in close proximity to another three, and a bunch of others, may not, in the opinion of some, fit within the constraints of the table. I agree with Don's interpretation of when it can or can't be used for an underground ductbank. I also agree with Dennis's statement about the annex being the purview of engineers.stanrat said:. . . says that I can use 310.16 for ampacities . . . .