TheWantonElectrician
Member
- Location
- Madison, WI
- Occupation
- Master Electrician (Residential and small-scale commercial)
2017 NEC: Annex example D8
Question 1: Under the Branch-Circuit Short-circuit and Ground-fault Protection section, is there a reason to not work out the selection for the 30-hp motors? I calculated them to need a 125A nontime-delay or 70A time-delay protective device. Can anyone confirm this selection?
Question 2: This might get answered from Q1's answer, but why does the Feeder Short-circuit and Ground-fault Protection section use the 25-hp motor's protective device rating rather than the protective device for one of the 30-hp motors (which I assume to have a largest BC protective device)? I calculated the feeder to need a 175A nontime-delay protective device. Can anyone confirm this selection?
Question 3: The nameplate secondary full load current is given for the 30-hp motors. How can I use this information for motor calculations?
I have read through the following thread and think my questions may be related, but I still don't really understand it: https://forums.mikeholt.com/threads...nd-rotor-load-left-out-of-feeder-calc.103192/
Question 1: Under the Branch-Circuit Short-circuit and Ground-fault Protection section, is there a reason to not work out the selection for the 30-hp motors? I calculated them to need a 125A nontime-delay or 70A time-delay protective device. Can anyone confirm this selection?
Question 2: This might get answered from Q1's answer, but why does the Feeder Short-circuit and Ground-fault Protection section use the 25-hp motor's protective device rating rather than the protective device for one of the 30-hp motors (which I assume to have a largest BC protective device)? I calculated the feeder to need a 175A nontime-delay protective device. Can anyone confirm this selection?
Question 3: The nameplate secondary full load current is given for the 30-hp motors. How can I use this information for motor calculations?
I have read through the following thread and think my questions may be related, but I still don't really understand it: https://forums.mikeholt.com/threads...nd-rotor-load-left-out-of-feeder-calc.103192/