does anyone have a copy of article 220-30 concerning residential load calcs. you can fax me or post ?
 

ctroyp

Senior Member
Re: NEC Art. 220-30

From 2002 NEC
III. Optional Calculations for Computing Feeder and Service Loads
220.30 Optional Calculation ? Dwelling Unit.
(A) Feeder and Service Load. For a dwelling unit having the total connected load served by a single 3-wire, 120/240-volt or 208Y/120-volt set of service or feeder conductors with an ampacity of 100 or greater, it shall be permissible to compute the feeder and service loads in accordance with this section instead of the method specified in Part II of this article. The calculated load shall be the result of adding the loads from 220.30(B) and (C). Feeder and service-entrance conductors whose demand load is determined by this optional calculation shall be permitted to have the neutral load determined by 220.22.
(B) General Loads. The general calculated load shall be not less than 100 percent of the first 10 kVA plus 40 percent of the remainder of the following loads:
(1) 1500 volt-amperes for each 2-wire, 20-ampere small-appliance branch circuit and each laundry branch circuit specified in 220.16.
(2) 33 volt-amperes/m2 or 3 volt-amperes/ft2 for general lighting and general-use receptacles. The floor area for each floor shall be computed from the outside dimensions of the dwelling unit. The computed floor area shall not include open porches, garages, or unused or unfinished spaces not adaptable for future use.
(3) The nameplate rating of all appliances that are fastened in place, permanently connected, or located to be on a specific circuit, ranges, wall-mounted ovens, counter-mounted cooking units, clothes dryers, and water heaters.
(4) The nameplate ampere or kVA rating of all motors and of all low-power-factor loads.
(C) Heating and Air-Conditioning Load. The largest of the following six selections (load in kVA) shall be included:
(1) 100 percent of the nameplate rating(s) of the air conditioning and cooling.
(2) 100 percent of the nameplate ratings of the heat pump compressors and supplemental heating unless the controller prevents the compressor and supplemental heating from operating at the same time.
(3) 100 percent of the nameplate ratings of electric thermal storage and other heating systems where the usual load is expected to be continuous at the full nameplate value. Systems qualifying under this selection shall not be calculated under any other selection in 220.30(C).
(4) 65 percent of the nameplate rating(s) of the central electric space heating, including integral supplemental heating in heat pumps where the controller prevents the compressor and supplemental heating from operating at the same time.
(5) 65 percent of the nameplate rating(s) of electric space heating if less than four separately controlled units.
(6) 40 percent of the nameplate rating(s) of electric space heating if four or more separately controlled units.
 