Can FMC be used, as a barrier, in a Pull Box that has normal and emergency power?
Can FMC be used, as a barrier, in a Pull Box that has normal and emergency power?
Im going to strongly have to say NO!! Emergency and Normal Power has to be COMPLETELY independent of each other, save for a few exceptions (ie transfer switches).
Just how "COMPLETELY independent" ? Maybe it should be in a different building? You don't even know the details yet.
Brother, say you had a surface mounted raceway going to the gantry of an xray machine, if you install a normal branch circuit in FMC along side open critical branch conductors in this raceway, they are effectively separated and independent of each other and 517.30(C)(1) is satisfied.
Of course the proper way to do it would be to use dividers (barriers) for the separation
Roger