Mauricio Solis
New member
We need some clarification and interpreation on this conflict:
NEC NFPA 70 Article 630-15: "Objectionble current in welding output circuit"
ANSI Z49.1
11.3.2 The Work. The work piece or metal upon which the welder welds shall be grounded independent of the welding leads to a good electrical ground., unless a qualified person assures it is safe to work on ungrounded work piece.
Miller O&M manual Section 8 (OMB-356) recommends to connect the work piece to a building to address AC High Frequency.
Grounding and Arc Welding Safety:
Grounding the workpiece has similar benefit to grounding the welding machine enclosure. When the workpiece is grounded, it is at the same potential as other grounded objects in the area. In the event of insulation failure in the arc welding machine or other equipment, the voltage between the workpiece and ground will be limited.
Question:
If we follow the code and removed the ground wire connection between table and building ground and totally isolate weld table, how do you address difference in potential and AC high frequency that needs to dissipate to ground and can sometimes cause electric shock.
NEC NFPA 70 Article 630-15: "Objectionble current in welding output circuit"
ANSI Z49.1
11.3.2 The Work. The work piece or metal upon which the welder welds shall be grounded independent of the welding leads to a good electrical ground., unless a qualified person assures it is safe to work on ungrounded work piece.
Miller O&M manual Section 8 (OMB-356) recommends to connect the work piece to a building to address AC High Frequency.
Grounding and Arc Welding Safety:
Grounding the workpiece has similar benefit to grounding the welding machine enclosure. When the workpiece is grounded, it is at the same potential as other grounded objects in the area. In the event of insulation failure in the arc welding machine or other equipment, the voltage between the workpiece and ground will be limited.
Question:
If we follow the code and removed the ground wire connection between table and building ground and totally isolate weld table, how do you address difference in potential and AC high frequency that needs to dissipate to ground and can sometimes cause electric shock.