Dear all
We are in switzerland and we have a interpretation dilemma with the NFPA 70 (NEC 2011) art. 725.
We produce valve actuators (small servomotor) with a fixed CL2 cable "pigtail" of 3 meters.
Our actuators works with 24Vac in Class 2 circuits. They have a nominal power consumption of 15W.
Its is for us not clear if for our CL2 UL listed cable pigtail,
conductors with a cross section of 20AWG are allowed or not? (need we AWG18)
We are very gradeful for all help that you can give us.
Thank you very much and best regards from switzerland
:?
J-L ucuu