I have an electrical room with a 480/277 volt busway in an electrical room on a floor in a high rise office building.
The bus way feeds a 400 amp 480/277 volt panel for lighting and mechanical loads as well the busway feeds a 400 amp 208/120 volt panel through a 112.5 kva transformer.
The bus way is located in the electrical room so that it has the code required clearances in front of it with the bus way disconnects installed.
With the change in NEC Article 110.26(C)(2), will the fact that the bus way is rated 1200 amps or larger now require that I have double the working clearance in front of the bus way and associated disconnects?