I have seen several different methods for circuiting electric fan powered mixing boxes, some of which I don't feel are correct.
If I put both of these boxes on a 30A-3P circuit with (4)#10,(1)#10G-3/4"C am I in violation of the NEC? I have also been told that I need a fused disconnect at each FPMB. Is this correct? If so, where in the code is this stated?
If I were to provide power for a single FPMB at 20kW with a 1/2 HP fan I would provide a 40A-3P circuit with (4)#8,(1)#10G.-3/4"C to the unit. Would I need a fused disconnect at this unit?
Hopefully this leads to some good discussion. I searched for several hours, but could find a definitive answer.
- I have an open office space with (2) FPMB at 480,3PH each with a 1/8 HP fan at 277,1PH
- FPMB-1 and FPMB-2 both have 8kW heaters
- Both boxes are specified with factory interlocking main disconnect switch.
If I put both of these boxes on a 30A-3P circuit with (4)#10,(1)#10G-3/4"C am I in violation of the NEC? I have also been told that I need a fused disconnect at each FPMB. Is this correct? If so, where in the code is this stated?
If I were to provide power for a single FPMB at 20kW with a 1/2 HP fan I would provide a 40A-3P circuit with (4)#8,(1)#10G.-3/4"C to the unit. Would I need a fused disconnect at this unit?
Hopefully this leads to some good discussion. I searched for several hours, but could find a definitive answer.