I understand that article 450 provides guidance for sizing overcurrent protection devices for transformers. However, I didn't see any discussion on the location of the said protective devices. Say the circuit breaker providing primary protection to the transformer is located in the MCC, than this breaker would need to be sized such that it protects the feeder to the transformer as well. This would mean that the primary breaker functions not only as the protective device for the transformer but also for conductor protection. I didn't see any requirements in the article that the protective devices need to be installed AT the transformer.
Am I missing something?
It appears to me that both the transformer and the primary& secondary wiring need to be treated as one when sizing the breakers/fuses.
Thanks,
EE
I understand that article 450 provides guidance for sizing overcurrent protection devices for transformers. However, I didn't see any discussion on the location of the said protective devices. Say the circuit breaker providing primary protection to the transformer is located in the MCC, than this breaker would need to be sized such that it protects the feeder to the transformer as well. This would mean that the primary breaker functions not only as the protective device for the transformer but also for conductor protection. I didn't see any requirements in the article that the protective devices need to be installed AT the transformer.