NEC Article 964 Small Wind Systems - What size main panel to use?

Status
Not open for further replies.

SGEI

Member
Location
Phelan CA USA
Hello all,

Thanks for offering this great forum. I've browsed around here quite a bit over the last few months and have gained quite a bit of info.

I understand that the 2011 NEC includes provisions for small wind energy systems, article 964.


However, I can't figure this problem out.
I have a question relating to what size the main should be for a 10 kW 240v grid tie wind system.

Is it okay to have the wind system on a 60 amp breaker with the main being a 200 amp panel?

I understand that section 690? states that solar energy system breaker size is not to exceed 20% of the main panel amperage. Is this the same story for small wind systems too?


Thanks in advance,

Steve
 
Y
Hello all,

Thanks for offering this reat forum. I've browsed around here quite a bit over the last few months and have gained quite a bit of info.

I understand that the 2011 NEC includes provisions for small wind energy systems, article 964.


However, I can't figure this problem out.
I have a question relating to what size the main should be for a 10 kW 240v grid tie wind system.

Is it okay to have the wind system on a 60 amp breaker with the maintaining being a 200 amp panel?

I understand that section 690? states that solar energy system breaker size is not to exceed 20% of the main panel amperage. Is this the same story for small wind systems too?


Thanks in advance,

Steve
If the 200A panel has only a 200A busbar, then the maximum size for the backfed breaker is 240A minus the size of the main breaker.
Put in a 100A main and you can use up to 140A for the RE breakers. (Not that that would make a lot if sense.)

The calculation should apply to any GTI whether solar, wind, or water powered.

The 120% only applies if there are other loads on the pa el. If it is e.timely a backfeed combiner, a different calculation applies.
 
Last edited:
My local utility states that since the system breaker ( its a 60 amp ) exceeds 20 % of the main bus amperage its not to NEC code.
Assuming that the panel bus is rated at 200 amps and there is a 200 amp main breaker, they are correct.
 
Looks like the panel has a 225 amp bus with a 200 amp main breaker. So if my calculations are correct, I should be okay up to 70 amps line feed from the turbine.
 