JEFF MILLAR
Senior Member
The NEC specifically address Continuous Loads and requires 125 % increase in the Ampacity.
Plus additional Ampacity derating factors for Ambient temp. and the spacing / separation / cables touching .
Apparently the IEC does not consider continuous duty and requires only the circuit Ampacity be corrected for the method of installation and provides detailed tables for installation method. Example correction. tables are provided for , direct burial, depth below ground, ground temperature , soil thermal resistivity, and spacing between cables. Apparently this is how IEC derates the cable Ampacity. There is no correction for continuous load. I have seen IEC cable calculations with the derating tables applied to correct the Ampacity and then also 125 % included for continuous duty. I do not believe the IEC requires this additional 125 % correction. Any experience you can share on this would be very helpful. Thank you in advance.
Plus additional Ampacity derating factors for Ambient temp. and the spacing / separation / cables touching .
Apparently the IEC does not consider continuous duty and requires only the circuit Ampacity be corrected for the method of installation and provides detailed tables for installation method. Example correction. tables are provided for , direct burial, depth below ground, ground temperature , soil thermal resistivity, and spacing between cables. Apparently this is how IEC derates the cable Ampacity. There is no correction for continuous load. I have seen IEC cable calculations with the derating tables applied to correct the Ampacity and then also 125 % included for continuous duty. I do not believe the IEC requires this additional 125 % correction. Any experience you can share on this would be very helpful. Thank you in advance.