Sparky2791
Senior Member
- Location
- Northeast, PA
- Occupation
- Electrical Design
Having a debate regarding these calculations.
If the final calculations for the school based on this section come to 208,550vA or 579A @ 120/208V 3Phase is a service disconnect of 600A permitted? Assuming you are sizing the buildings service for the smallest service NEC allows? Obviously the 600A service disconnect allows little room for additional loads.
Thanks for reading.
If the final calculations for the school based on this section come to 208,550vA or 579A @ 120/208V 3Phase is a service disconnect of 600A permitted? Assuming you are sizing the buildings service for the smallest service NEC allows? Obviously the 600A service disconnect allows little room for additional loads.
Thanks for reading.