NEC Chap 9 Table 9

Status
Not open for further replies.

MyCleveland

Senior Member
Location
Cleveland, Ohio
Do wire manufacturers produce similar tables for first 8 columns for different insulation types ?

What effect if six, nine, etc, conductors of same or different sizes ?
How to calculate ?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
What are the different insulation types you are looking for? If the insulation isn't listed in the NEC then it probably isn't compliant.


If you have more than 3 current carrying conductor's ion a raceway you have to de-rate per table 310.15(B)(3)(a)

You calculate based on Chapter 9, Tables 4 and 5 for mixed sizes. Where the wires are all the same size you can use Annex C
 

MyCleveland

Senior Member
Location
Cleveland, Ohio
Dennis
Thanks for responding....

Chap 9-Table 9, notes state table is good for "RHH" wires.
These values are representative of all 600V wiring insulation types ? or are there tables for each type, THHN, XHHW, etc. ?

I understand derating issue, but was wondering if tables exist for effect on impedance values when adding additional wires of same or different sizes ?

Tables 4, 5 and Annex C do not address impedance issue.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Dennis
Thanks for responding....

Chap 9-Table 9, notes state table is good for "RHH" wires.
These values are representative of all 600V wiring insulation types ? or are there tables for each type, THHN, XHHW, etc. ?

I understand derating issue, but was wondering if tables exist for effect on impedance values when adding additional wires of same or different sizes ?

Tables 4, 5 and Annex C do not address impedance issue.
In general adding more wires or limiting cooling has no effect whatsoever on impedance.


Sent from my XT1585 using Tapatalk
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Thank you GoldDigger

Going through some papers on a wire manufacturer web site seemed to imply this was an issue.
Running an isophase arrangement where all of the set conductors for one phase run in a separate duct can very slightly increase the inductance over having all of the conductors of a circuit being in the same duct, FWIW.

Sent from my XT1585 using Tapatalk
 