Isn't there something in here that specifically states that one connot run communication circuits in the same drilled studs as line voltage circuits :?
Cat 5no not that I know of; Why would you not be allowed to run these cables in the same drilled holes. Some applications would spec the low voltage to be shielded cable
Isn't there something in here that specifically states that one connot run communication circuits in the same drilled studs as line voltage circuits :?
Isn't there something in here that specifically states that one connot run communication circuits in the same drilled studs as line voltage circuits :?
725.136(I) would apply to the application in question.725.136(A) ??
(I) Other Applications. For other applications, conductors of Class 2 and Clas s 3 circuits shall be separated by at least 50 mm (2 in.) from conductors of any electric light, power, Class 1 non?power-limited fire alarm or medium power network-powered
broadband communications circuits unless one of the following conditions is met:
(1) Either (a) all of the electric light, power, Class 1, non?power-limited fire alarm and medium -power networkpowered
broadband communications circuit conductors or (b) all of the Class 2 and Class 3 circuit conductors are in a raceway or in metal-sheathed, metal-clad, non?metallic-sheathed, or Type UF cables.
...