Chapter 9 note 7 in the NEC is kind of confusing in my opinion. From an example it shows the quantity of wires that will fit within the size. This is done by taking the conduits fill area divided by the conductors area to find the number of conductors able to fit. For example, 1.25" RMC at 40% fill is 0.610. The area of a #10 AWG is 0.0211. These divided is equal to 28.91, which given that the decimal is over .8, you can fit 29 conductors within it.
I am trying to apply this math a different way, and I want to see if it "maths" out. My problem is:
I have (4) 600 KCMIL conductors and a #3 AWG grounding conductor. The total area from these conductors is 4.005 (4*0.9729+0.1134 (these values derived from Chapter 9 Table 5 THW section). Then, moving to Chapter 9 Table 4, the 40% fill for a 3" conduit is 3.538. Shucks, it is too small. However, if I divide the 3.538 by 4.005, I get 0.8834. Since this is above .8, am I allowed to use the 3" conduit? Or should I play it safe an use a 3.5" conduit because its permittance is 4.618 which gives ample space?
I am trying to apply this math a different way, and I want to see if it "maths" out. My problem is:
I have (4) 600 KCMIL conductors and a #3 AWG grounding conductor. The total area from these conductors is 4.005 (4*0.9729+0.1134 (these values derived from Chapter 9 Table 5 THW section). Then, moving to Chapter 9 Table 4, the 40% fill for a 3" conduit is 3.538. Shucks, it is too small. However, if I divide the 3.538 by 4.005, I get 0.8834. Since this is above .8, am I allowed to use the 3" conduit? Or should I play it safe an use a 3.5" conduit because its permittance is 4.618 which gives ample space?