| Sorry.What I wanted to say in the "cradle" it is the average. |
I remember studying this stuff on my PE a while ago and doing practice problems lol.However, the manufacturer engineering handbook it is better. See calculation way per Okonite catalogueView attachment 2569349
In theory, what would the worst worst worst case scenario?If it's for short circuit calc purposes, why not just use the non-magnetic reactance? You'll be conservative. If the results don't put you into the next size AIC rating, call it a job well done.
Superconductors = boomIn theory, what would the worst worst worst case scenario?
Would it be bare non-insulated copper conductors in free air?
Well I mean realistic worst case scenarios.. lolSuperconductors = boom
So worst case would be liquid helium around the wire.
JR, hope you are well...In order to calculate the maximum, short-circuit currents, according to IEC 60909-0, the resistance of lines(overhead lines and cables) are to be introduced at a temperature of 20oC.
Reactance minimal is then in equilateral triangle case.
IEEE 141/1993 Chapter 4 Short-circuit current calculations
4.5.2 Step 2:Collect and convert impedance dataView attachment 2569369