For a current project, an existing 25HP blower (continuous) is installed with a 100A breaker. Per NEC 430.250 the FLC, is 34A meaning the 250% breaker sizing would be 85A. I believe the 100A was chosen as the motor will be replaced in the future to 50HP.
Questions:
Thanks!
Questions:
- For the current setup, is the 100A acceptable per NEC code OR should the breaker size be reduced to 80A?
- If the load was not continuous would the 100A be acceptable?
Thanks!