I'm currently working on a job where an existing panelboard has
Bus - 1200amp rated
3 - 400amp fusible switches
1 - 250amp fusible switch
2 - 100amp fusible switches
3 * 400 + 250 + 2 * 100 = 1650amps
1650 amps - 1200amps = 450amp over rating
Would this be against NEC code. I see some old projects where its common to have circuit breakers in a panel that exceed the bus bar rating.
Here are some code sections I found:
This says no but it refers to PV systems.
NEC 705.12(D) (3) Busbars. One of the methods that follow shall be used to determine the ratings of busbars in panelboards
Here it basically says it depends on the manufacturer
NEC 2014 408.54 Maximum Number of Overcurrent Devices. A panelboards shall be provided with physical means to prevent the installation of more overcurrent devise than that number for which the panelboard was designed, rated, and listed.
For the purposes of this section, a 2-pole circuit breaker or fusible switch shall be considered two overcurrent devices; a 3-pole circuit breaker or fusible switch shall be considered three overcurrent devices.
Bus - 1200amp rated
3 - 400amp fusible switches
1 - 250amp fusible switch
2 - 100amp fusible switches
3 * 400 + 250 + 2 * 100 = 1650amps
1650 amps - 1200amps = 450amp over rating
Would this be against NEC code. I see some old projects where its common to have circuit breakers in a panel that exceed the bus bar rating.
Here are some code sections I found:
This says no but it refers to PV systems.
NEC 705.12(D) (3) Busbars. One of the methods that follow shall be used to determine the ratings of busbars in panelboards
- The sum of 125 percent of the inverter(s) output circuit current and the rating of the overcurrent device protecting the busbar shall not exceed the ampacity of the busbar.
- Where two sources, one a utility and the other an inverter, are located at opposite ends of a busbar that contains loads, the sum of 125 percent of the inverter(s) output circuit current and the rating of the overcurrent device protecting the busbar shall not exceed 120 percent of the ampacity of the busbar. The busbar shall be sized for the loads connected in accordance with Article 220. A permanent warning label shall be applied to the distribution equipment adjacent to the back-fed breaker form the inverter that display the following or equivalent wording.
Here it basically says it depends on the manufacturer
NEC 2014 408.54 Maximum Number of Overcurrent Devices. A panelboards shall be provided with physical means to prevent the installation of more overcurrent devise than that number for which the panelboard was designed, rated, and listed.
For the purposes of this section, a 2-pole circuit breaker or fusible switch shall be considered two overcurrent devices; a 3-pole circuit breaker or fusible switch shall be considered three overcurrent devices.