I need a sanity check. We are installing a new 120/208 3P panel, and plan to pull all spare circuits out of the panel to a JB, so as to avoid the need for a shutdown in the future. I am being told its ok to pull (20) #10s (single phase 20A circuits) + (1) #10 G in a 2" EMT to a large JB 60' away from the panel. I know it's in the code book that states this is not code compliant, due to derating.My thought was to use (6) #10s + (1) #10G in 1" EMT for how ever many spares pulled out. Thank you for the response