NEC CODE for 200kw UPS

Status
Not open for further replies.
I am installing a 200KW UPS 480 in 480 out. I am going to have a 400 AMP 480 three phase Enclosed Circuit Breaker/disconnect installed to provide it power. The UPS system is going to be placed inside a cage along with 18 computor racks. The cage is 20Ft wide and forty ft long. Is there a code that states the distance the ECB/Disconnect has to be in referense to the UPS?

Thanks
 
What provides the overcurrent protection for the output conductors? If it is your ECB, then the rules in 240.21(B) will apply.
 