dnormanGT_ATL
New User
- Atlanta, GA
- Estimator/Project Manager
On a multi-family highrise renovation job in Atlanta, the engineer of record issued a late in the schedule change as they realized they undersized the natural gas generator for the building. We are now being told to provide a 300kW nat gas genset with (2) separate breakers (400A/3P for emergnecy panels, 300A/3P for fire pump) feeding (1) new 800A manual transfer switch. The manufactuer of MTS (Trystar) has stated that this design does not meet NEC code and that we will have to go with just (1) breaker (800A/3P) in the genset and then have a 400A/3P and 300A/3P breaker built into the MTS. Trystar has not said what code they are referencing, however, it would make sense that if we fed the MTS with (2) separate breakers then when the owner has scheduled maintenance, they would have to rent (2) generators to keep the entire MTS backed up....but other than that I've been trying to figure out any other practical reason and what NEC code the manufactuer may be using to determine the current design does not meet NEC? Any thoughts? Thanks