I have a Motor Control Center with the following
503.4 Full Load Amps
I also need to add a lighting and airconditioning circuit that requires 55 Amps.
This will be feed to a separate circuit breaker box but the feed to this will be after the main circuit breaker.
Total Load - 558.3 Amps.
I am using individual Square D Magnetic Trip Manual starters that are specified for each motor in a range of 75 HP down to 6 HP. What is the rating neeed for the Feeder Protection? I would like to use a circuit breaker for the protection device. Is a 600 AMP circuit breaker large enough? I need this to meet NEC code requirements.
503.4 Full Load Amps
I also need to add a lighting and airconditioning circuit that requires 55 Amps.
This will be feed to a separate circuit breaker box but the feed to this will be after the main circuit breaker.
Total Load - 558.3 Amps.
I am using individual Square D Magnetic Trip Manual starters that are specified for each motor in a range of 75 HP down to 6 HP. What is the rating neeed for the Feeder Protection? I would like to use a circuit breaker for the protection device. Is a 600 AMP circuit breaker large enough? I need this to meet NEC code requirements.