Hello Experts,
I recently stumbled across a residential install situation. If anyone has NEC code references to support the install or deem it in violation of the NEC your input would be greatly appreciated.
Homeowner installed a 2 pole 20 amp GFCI breaker in the main house panel. Then ran a 12-3 UF wire with ground 150ft. from the main house panel to a post near the lake to power a 240 volt Irrigation pump plugged into a 250 volt twist lock receptacle. Pump has cord and plug. Then proceeded to take one leg of 120 volts with a neutral, and ground wire to a 120 volt GFCI receptacle into another box next to the irrigation receptacle box.
I questioned this method of tapping off one leg of a 240 volt circuit with no over current protection for the 120 volt circuit which was created.
Is this code compliant to do this type of wiring methods? I would have installed a small 6 circuit sub panel with breakers to feed the pump and the GFCI outlet to protect the tapping off of the 240 volts.
I have searched and asked the local inspector about this but the inspector can't think of why this can't or shouldn't be done this way.
If anyone has NEC code articles I could look up would be greatly appreciated.
Thanks
Rdub
I recently stumbled across a residential install situation. If anyone has NEC code references to support the install or deem it in violation of the NEC your input would be greatly appreciated.
Homeowner installed a 2 pole 20 amp GFCI breaker in the main house panel. Then ran a 12-3 UF wire with ground 150ft. from the main house panel to a post near the lake to power a 240 volt Irrigation pump plugged into a 250 volt twist lock receptacle. Pump has cord and plug. Then proceeded to take one leg of 120 volts with a neutral, and ground wire to a 120 volt GFCI receptacle into another box next to the irrigation receptacle box.
I questioned this method of tapping off one leg of a 240 volt circuit with no over current protection for the 120 volt circuit which was created.
Is this code compliant to do this type of wiring methods? I would have installed a small 6 circuit sub panel with breakers to feed the pump and the GFCI outlet to protect the tapping off of the 240 volts.
I have searched and asked the local inspector about this but the inspector can't think of why this can't or shouldn't be done this way.
If anyone has NEC code articles I could look up would be greatly appreciated.
Thanks
Rdub