NEC code sections for lighting/power for working area in a shipping container

Status
Not open for further replies.

fandi

Senior Member
Location
Los Angeles
Occupation
Electrical Engineer
Hello All,
One company decided to let their employees work in a shipping container. The container is inside a typical inland building. The reason is the owner can relocate the container with him in a few years. Do you know what NEC code sections applicable for the lighting/power? The service rating is about 400A single phase 208/120V.
Thanks.
 
Last edited:
I've never done one, but I've seen a lot of them. Not uncommon in the oil fields in the Midwest. All of them I've seen have all been RMC through out the entire container with seal offs. That's because of the location they're being used, normally classified as 1D1.

Jason
 