Bruce Lorraine
Question, which is right?
NEC
When operating multiple vehicles at the same location and each is operating off their individual onboard generators, never connect the vehicles to the same ground electrode subsystem because of differences of electrical potential. (NEC section 250.34, page 70-103)
Military (A Guide to Proper Earth Grounding and Bonding Methods for Use with Tactical Systems CECOM TR-98-6)
Interconnecting the ground rods for different shelters helps to create an earth grounding electrode system having an overall lower grounding resistance, and results in other benefits as well. Therefore, where electronic equipment shelters are located within 25 feet of each other, it is recommended that the individual earth grounding electrodes be bonded together using a heavy copper conductor (6 AWG minimum) run along the ground.
If more than 1 truck (each with own gen set) are operating within 25 feet of each other, do they need to use a common bond/ground? (Radio and IT systems operating)
			NEC