R rkehs New member Oct 26, 2010 #1 i am looking at article 300.3 letter C. my question is can i run 120v along with 24 volt in the same conduit as long as the insulation rating is 300v ?? please help rkehs
i am looking at article 300.3 letter C. my question is can i run 120v along with 24 volt in the same conduit as long as the insulation rating is 300v ?? please help rkehs
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Oct 26, 2010 #2 At the bottom of 300.3(C)(1) there's an FPN. Check out what Article 725 has to say about it. Welcome to the Forum.
At the bottom of 300.3(C)(1) there's an FPN. Check out what Article 725 has to say about it. Welcome to the Forum.
raider1 Senior Member Staff member Location Logan, Utah Oct 26, 2010 #3 Welcome to the forum. Check out 725.130(A) Exception #2 and 725.136. Chris