Outdoor commercial landscape lighting - Can you run 120 volt & 277 volt in the same conduit?
What about the conductors being fed from separate sources or panel?
I want to say yes. A contactor panel could have 277 lighting contactor loads and 120v time clock closing the contactors.What about the conductors being fed from separate sources or panel?
I want to say yes. A contactor panel could have 277 lighting contactor loads and 120v time clock closing the contactors.
Motor starters are similar ,,277/480 load with 120 aux holding circuit..But I would have to look it up to be sure.
I want to say yes. A contactor panel could have 277 lighting contactor loads and 120v time clock closing the contactors.
Motor starters are similar ,,277/480 load with 120 aux holding circuit..But I would have to look it up to be sure.
YesWhat about 480 ac feeder with gfci circuit piped up to the roof ?
What about 480 ac feeder with gfci circuit piped up to the roof ?
That is only correct when you are talking about power system conductors. There are restrictions where you are mixing power system and remote control and signaling conductors.You can mix voltages in a conduit in boxes under any condition. Doesn't matter what application or scenario you might think up. All boxes must be labeled with the ckt and panel #. Color code must be labeled at the panel. All insulation must be the same for the higher voltage.
Dennis stole my answer, but he always does that.I changed your text to sentence case because the upper case is hard to read.
If you have both voltages in the jb then are the color coated properly for the different voltages? If not then you may want to put a tag or label in the boxes or tape the 277 v system with different color code