R Rai136926 Member Location seattle, wa Nov 13, 2014 #1 Which NEC table would I need to use if I am running single conductor copper 15kv cable running it in underground conduit duct bank?
Which NEC table would I need to use if I am running single conductor copper 15kv cable running it in underground conduit duct bank?
M MR. S Member Location Connecticut Nov 14, 2014 #2 Table 300.50 shows minimum cover requirements over 600. FYI I am using the 2011 NEC
Smart $ Esteemed Member Location Ohio Nov 14, 2014 #3 Read the conditions stated in the titles of Tables 310.60(C)(67) through (86). Use the one that matches your installation.
Read the conditions stated in the titles of Tables 310.60(C)(67) through (86). Use the one that matches your installation.