NEC Conductor Colours
We have sold a dimmer unit to the US and I am looking for details on Conductor Colours
Our standard 3 phase cable is
Neutral Blue
Earth Gn/Yel
Phase1 Brown
Phase2 Black
Phase3 White
I am told the Neutral in the US is White
I am currently looking through the NEC2002 book for details
Can anyone supply details on what colours can and can not be used for the different conductors and what section in the NEC book this info can be found
Thank you to anyone who can help
Re: NEC Conductor Colours
Ran into your blue neutral other day.Someone drove off on a lift with charger still pluged in.Sounds simple to fix till your looking at blue,yellow /green and forgot the other one.Fixed it but did make me think a few minutes and ohmed it out
still looking through the NEC book
Neutral White
Earth Gn/Yel
Phase1 ?
Phase2 ?
Phase3 ?
can anyone tell what section may cover this?
actually, if it is part of a manufactured system as opposed to an installation, none of the NEC requirements would apply.
UL allows lt blue to be used for power cords if I am not mistaken.
400.22(C) of '05 NEC does recognize a light blue grounded conductor in an appliance cord.
Where I usually run into them is in "foreign-type" equipment.
David,
Phase 1 Black
Phase 2 Red
Phase 3 Blue
Grounded/Neutral White
These are for 120vac. 3ph 4wire system.
Originally posted by benaround:
Phase 1 Black
Phase 2 Red
Phase 3 Blue
Frank unless you have local amendments that is just habit.
You can identify any voltage brown, orange, yellow or pink, violet, tan.
You can also make them all one color, it is up to the installer or job specifications. :)
I just returned from Ghana, Accra Africa blue in fixtures and appl. is the neutral and brown is the hot. On the 3 phase system we worked on the colours used where brown red yellow and white for the neutal. It changed alot so dont quote the phase1,2,3.
Having gone through NECA/IBEW apprenticship training (20 + years ago) , I was taught and have always found the following:
120v/208/220 - Black, Red , Blue, White netural and Green gnd,
480/277 and up
Brown, Orange, Yellow, Gray neutral and Green gnd.
There are a number for sections that dictate the correct color coding for the GROUNDED conductor, as well as the Highleg. But this is the only written information I found on the UNGROUNDED conductors.
210.4(D) Identification of Ungrounded Conductors. Where more than one nominal voltage system exists in a building, each ungrounded conductor of a multiwire branch circuit, where accessible, shall be identified by phase and system. This means of identification shall be permitted to be by separate color coding, marking tape, tagging, or other approved means and shall be permanently posted at each branch-circuit panelboard.
Larry Zuravin
Latham International
Maintenance Supervisor
Scotia, NY
Larry, What you desrcbibe is common trade practice, but as you discovered in not required by the NEC.
The bottom line is that the NEC allows electricians and designers our choice of colors for ungrounded conductors, and that's exactly how it should remain.
The NEC is not a design manual, and it would be a major stretch to say that insulation color has anything to do with safety. In fact, it's been argued many times here that requiring a color code may actually decrease safety, because electricians will then rely on an assumption (insulation color) rather than on their testers.
Peter,
I do agree that this is a trade practice. As we have read, the NEC is really more concerned about identifying the Neutral and ground. You are right that the colors aren't specified for ungrounded conductors, but I believe that adhering to a standard, weather it is B/R/B or B/O/Y, is important in that it identifies phasing ( and that could also be done numerically, 1,2,3 or alphabetically, A,B,C), identifies the ungrounded conductor, as well as (in my opinion) presenting an asthethicly pleasing, professional looking and organized load center. And speaking of good practices, I wholeheartedly agree about using your tester. All I speak of is the practices I've encountered in the Northeast. Though I would hope that if I went to another part of the country, that what ever the practices of that area were, that they would be consist ant.
Larry
For internal control panel wiring, neither UL508A nor NFPA79 "suggest" coloring coding of phase conductors, they prefer other means of identifying circuits. They do have specific requirements for colors of grounded and grounding conductors.
Their recommendations include:
Black for all ungrounded conductors at supply voltage
Red for all ungrounded AC conductors at less than supply voltage
Blue for all ungrounded DC conductors
Yellow for all ungrounded conductors that remain energized when main disconnect is "off".