Howdy y'all, I have to do a cost estimate for all the materials need electrically on a project. There are 4 additional panels being added to the facility. I have ran into a couple of questions on the way for conductor and conduit sizing.
All panels are 208Y/120V, so that makes them three phase (I believe... in the one line diagram, only one panel states it is three phase, the others do not have any markings about phase). From my understanding, that would require three conductors, one for each phase. Also, I question the necessity for a grounding conductor, I have seen that panels don't require one (online) but for some reason that does not feel right. So now, each control panel has at least 4 wires in its conduit, 3 for each phase and 1 for ground.
At this point, I did not consider derating, even though there are 4 or more wires ( NEC Table 310.15(B)(3)(a) ). I did this because I believe one of the wires is not technically a current carrying conductor. Now, was time for sizing the conductors with table 310.15(B)(16). The calculation I feel most confident was for 400A panel. I sized it with 600 KCMIL because they handle 420A (75 degrees column because circuit is above 100A). I then used table 250.66 for ground sizing, and got #1/0 cable. Further along, I moved to chapter 9 table 5, and calculated the area. 600 KCMIL at 0.9729 in^2 and #1/0 at 0.2223 in^2. The total area calculated to 3.141 in^2 (3*0.9729+0.2223). This fits under chapter 9 table 4's 3" EMT size for over 2 wires (3.538 in^2).
Now for some more confusion I have... there is a control panel at 1200A. Under table 310.15(B)16, there is no conductor rated purely for 1200A. So, I decided to go with 4 350 KCMIL in parallel. 350 KCMIL is rated for 310A so the 4 in parallel would be at 1240A. Now, for grounding, I used #2 conductor based from table 250.66 (also would need 4 of them I believe). Now here is the wacky stuff, there are 3 phases, each with 4 wires, so there is 12 conductors, then the 4 grounding conductors, so there is 16 total. This leads me to derate, which at that point, don't I have to migrate of the 90 degrees column in table 310.15(B)16? And then, even looking over that fact, if we size the conduit based around these conductors, the area fill is bigger than the 4" EMT in chapter 9 table 4. So do I have to use two conduits for this panel?
I know that was a lot to take in, but this is why I am stumped. I feel like I could be looking way too much into this but it is important and I want to do a good and thorough job (I am a new intern at an MEP firm). So a list form of my questions are:
All panels are 208Y/120V, so that makes them three phase (I believe... in the one line diagram, only one panel states it is three phase, the others do not have any markings about phase). From my understanding, that would require three conductors, one for each phase. Also, I question the necessity for a grounding conductor, I have seen that panels don't require one (online) but for some reason that does not feel right. So now, each control panel has at least 4 wires in its conduit, 3 for each phase and 1 for ground.
At this point, I did not consider derating, even though there are 4 or more wires ( NEC Table 310.15(B)(3)(a) ). I did this because I believe one of the wires is not technically a current carrying conductor. Now, was time for sizing the conductors with table 310.15(B)(16). The calculation I feel most confident was for 400A panel. I sized it with 600 KCMIL because they handle 420A (75 degrees column because circuit is above 100A). I then used table 250.66 for ground sizing, and got #1/0 cable. Further along, I moved to chapter 9 table 5, and calculated the area. 600 KCMIL at 0.9729 in^2 and #1/0 at 0.2223 in^2. The total area calculated to 3.141 in^2 (3*0.9729+0.2223). This fits under chapter 9 table 4's 3" EMT size for over 2 wires (3.538 in^2).
Now for some more confusion I have... there is a control panel at 1200A. Under table 310.15(B)16, there is no conductor rated purely for 1200A. So, I decided to go with 4 350 KCMIL in parallel. 350 KCMIL is rated for 310A so the 4 in parallel would be at 1240A. Now, for grounding, I used #2 conductor based from table 250.66 (also would need 4 of them I believe). Now here is the wacky stuff, there are 3 phases, each with 4 wires, so there is 12 conductors, then the 4 grounding conductors, so there is 16 total. This leads me to derate, which at that point, don't I have to migrate of the 90 degrees column in table 310.15(B)16? And then, even looking over that fact, if we size the conduit based around these conductors, the area fill is bigger than the 4" EMT in chapter 9 table 4. So do I have to use two conduits for this panel?
I know that was a lot to take in, but this is why I am stumped. I feel like I could be looking way too much into this but it is important and I want to do a good and thorough job (I am a new intern at an MEP firm). So a list form of my questions are:
- Does three phase inherently mean three conductors?
- Do control panels need a grounding conductor?
- Difference between grounding/neutral conductor (which one is NOT a current carrying conductor)?
- When breaking conductors to be in parallel (to carry sufficient current), is there a need to have multiple grounding conductors in parallel now?
- When you go over the 4 conductor threshold and need to derate, do you have to go to the 90 degrees column in table 310.15(B)16?
- What do you do when your area of more than 2 conductors exceeds the area for the max area of a conduit? (Ex: EMT has a max 4" conduit in chapter 9 table 4, with an area of 5.901 in^2, what should I do if my area of conductors is 6.7 in^2?)