I have a question on NEC cable protection for motor fed via ATS. As the conductor and upstream protective device settings for motor is sized differently than regular circuit.
A 600A upstream breaker feeds 400A ATS via 1 set of 500kcmil Copper cable (380A). The load side of ATS is connected to 300kVA chiller. The nameplate of the chiller says Min. Circuit Ampacity of 345A and Max. Circuit Breaker Size of 800A. My question is since the ATS feeds the motor which per nameplate is good thru 400A only (as per the sticker inside) is this still good per NEC.
My thoughts are the ATS is not protected by the upstream 600A breaker. I wanted to make sure I am thinking correctly since NEC on motors always stumps me.
I have a question on NEC cable protection for motor fed via ATS. As the conductor and upstream protective device settings for motor is sized differently than regular circuit.
A 600A upstream breaker feeds 400A ATS via 1 set of 500kcmil Copper cable (380A). The load side of ATS is connected to 300kVA chiller. The nameplate of the chiller says Min. Circuit Ampacity of 345A and Max. Circuit Breaker Size of 800A. My question is since the ATS feeds the motor which per nameplate is good thru 400A only (as per the sticker inside) is this still good per NEC.
My thoughts are the ATS is not protected by the upstream 600A breaker. I wanted to make sure I am thinking correctly since NEC on motors always stumps me.