Hello:
I am currently doing service calculations for a building which contains ~150 residential units and I wanted to get some opinions on how they should be classified. These are small single-room occupancy apartments, rented out long-term. The contain a sink, but no bathroom. The owner wishes to prepare the units to permit small "mini-kitchenette" units to be installed in the future. The kitchenettes combine a sink, small UC refrigerator, and two electrical cooktop burners and require only a single 120V, 15A circuit. These units will NOT have separate utility meters. Heating is via steam and there is no air conditioning (which precludes using the Optional Calc).
I'm going back and forth between calling these dwelling units (which would require including 3,000VA for SABC's to each unit) and including the mini-kitchenette's as fixed appliances (meaning only a 75% demand factor for the appliances to the service under 220.53) vs considering them to be more like dormitory units without the SABC's and using a 65% demand factor under 220.56. Unfortunately, the Article 100 definitions for both Dwelling Units and Guest Rooms require "sanitation" which these units do not have and, although used in the 2014 NEC, Dormitory Unit doesn't have an Article 100 definition.
I'm just curious if anyone else has done similar units before and could comment? I think I'm forced to treat these as Dwelling Units due to the cooking (even without a bathroom) but the combination of (2) SABC's and only being able to use a 75% load factor on the kitchenette's is going to require a very large service relative to how these units are actually utilized.
We're much more used to doing traditional multi-family dwelling or hotel units so I've never had to include one of these small "all in one" kitchenettes before but I realized that they create kind of an odd calculation issue. The total cooking load for this unit is only 1500W, which is less than the 1750W minimum required to use the demand factors in Table 220.55. Since this is fastened in place, it must fall under 220.53 and this results in a very large load. If the manufacturer increased the load of these units to include 1750W of cooking, then the total demand load in our example would drop from 169KVA (1500VA*150 units * 75% demand) to only 79KVA (1750VA * 150 units * 30%). This is quite a large difference. Since these are a planned future load anyway, I may well add in a future window PTAC unit for each unit too. This will allow me to use the Optional Calc's and with the 220.84 demand factor this produces a much lower load (basically free air conditioning from the NEC).
Thanks in advance for any comments.
I am currently doing service calculations for a building which contains ~150 residential units and I wanted to get some opinions on how they should be classified. These are small single-room occupancy apartments, rented out long-term. The contain a sink, but no bathroom. The owner wishes to prepare the units to permit small "mini-kitchenette" units to be installed in the future. The kitchenettes combine a sink, small UC refrigerator, and two electrical cooktop burners and require only a single 120V, 15A circuit. These units will NOT have separate utility meters. Heating is via steam and there is no air conditioning (which precludes using the Optional Calc).
I'm going back and forth between calling these dwelling units (which would require including 3,000VA for SABC's to each unit) and including the mini-kitchenette's as fixed appliances (meaning only a 75% demand factor for the appliances to the service under 220.53) vs considering them to be more like dormitory units without the SABC's and using a 65% demand factor under 220.56. Unfortunately, the Article 100 definitions for both Dwelling Units and Guest Rooms require "sanitation" which these units do not have and, although used in the 2014 NEC, Dormitory Unit doesn't have an Article 100 definition.
I'm just curious if anyone else has done similar units before and could comment? I think I'm forced to treat these as Dwelling Units due to the cooking (even without a bathroom) but the combination of (2) SABC's and only being able to use a 75% load factor on the kitchenette's is going to require a very large service relative to how these units are actually utilized.
We're much more used to doing traditional multi-family dwelling or hotel units so I've never had to include one of these small "all in one" kitchenettes before but I realized that they create kind of an odd calculation issue. The total cooking load for this unit is only 1500W, which is less than the 1750W minimum required to use the demand factors in Table 220.55. Since this is fastened in place, it must fall under 220.53 and this results in a very large load. If the manufacturer increased the load of these units to include 1750W of cooking, then the total demand load in our example would drop from 169KVA (1500VA*150 units * 75% demand) to only 79KVA (1750VA * 150 units * 30%). This is quite a large difference. Since these are a planned future load anyway, I may well add in a future window PTAC unit for each unit too. This will allow me to use the Optional Calc's and with the 220.84 demand factor this produces a much lower load (basically free air conditioning from the NEC).
Thanks in advance for any comments.