Long story short this facility I'm working has 9 substation with one common utility feeder. 7 of the transformers are 3 x 1-phase in a Delta-Delta configuration, mounted on a concrete pad with no secondary protection. Type THW and RHW feeders run from the transformer secondaries to a "bus gutter" where the feeders are taped to circuit breakers which are then fed to additional switch racks across the facility.
There is no apparent plant ground ring with each substation appearing to have its own isolated ground ring.
The other two transformers are 1 x 3-phase Delta-Delta, and a 1 x 3-phase Delta-Wye transformer solidly grounded.
1. I need help understanding 3 x 1 phase Delta-Delta configuration. How are these transformers typically grounded? The only grounds I can see are the case grounds. Are these grounds tied internally to the transformer wingdings? No ground is ran from the transformer to the switch racks.
2. I have both Delta-Delta and a Delta-Wye (solid grounded), what issues is expected with the facility being configured like this? I'm not exactly sure how the solidly ground transformer is tied.
2. The end goal is to have the facility "unmanned", is there something in the NEC about a facility being Delta-Delta configured? What risks are there to this?
3. Where is the line drawn at ownership of modifying existing electrical equipment that does not meet electrical code? I need to add motors to these existing switchracks, but the racks use a gutter type system where the incoming feeder is tapped to motor starters. I don't want to tie into existing taps as most of the existing installation violates the tap rule.
Thanks All
There is no apparent plant ground ring with each substation appearing to have its own isolated ground ring.
The other two transformers are 1 x 3-phase Delta-Delta, and a 1 x 3-phase Delta-Wye transformer solidly grounded.
1. I need help understanding 3 x 1 phase Delta-Delta configuration. How are these transformers typically grounded? The only grounds I can see are the case grounds. Are these grounds tied internally to the transformer wingdings? No ground is ran from the transformer to the switch racks.
2. I have both Delta-Delta and a Delta-Wye (solid grounded), what issues is expected with the facility being configured like this? I'm not exactly sure how the solidly ground transformer is tied.
2. The end goal is to have the facility "unmanned", is there something in the NEC about a facility being Delta-Delta configured? What risks are there to this?
3. Where is the line drawn at ownership of modifying existing electrical equipment that does not meet electrical code? I need to add motors to these existing switchracks, but the racks use a gutter type system where the incoming feeder is tapped to motor starters. I don't want to tie into existing taps as most of the existing installation violates the tap rule.
Thanks All