Does NEC require a minimum depth of footing for concrete encased electrode ground? pragraph number?
junkhound Senior Member Location Renton, WA Occupation EE, power electronics specialty Aug 16, 2023 #1 Does NEC require a minimum depth of footing for concrete encased electrode ground? pragraph number?
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Aug 16, 2023 #3 I would think that any footing built to building codes would meet the requirements.
M Malywr Senior Member Location New Jersey USA Aug 16, 2023 #4 LarryFine said: I would think that any footing built to building codes would meet the requirements. Click to expand...
LarryFine said: I would think that any footing built to building codes would meet the requirements. Click to expand...
J jaggedben Senior Member Location Northern California Occupation Solar and Energy Storage Installer Aug 16, 2023 #5 The answer is no, no NEC depth requirement. Only that the 'concrete foundation or footing' be 'in direct contact with the earth'.
The answer is no, no NEC depth requirement. Only that the 'concrete foundation or footing' be 'in direct contact with the earth'.