NEC Exhibit 700.2 requires separate vertical section for emergency ats load, legally required ats load, optional ats load...
Will this rule also apply for three branch of hospital ATS system? (Critical, Life-safety and Equipment branch), it appears to me critical and life-safety can be on same vertical section of switchboard? Thank you.
 
It depends on how the AHJ interprets 517.26.

517.26 Application of Other Articles.
The essential electrical
system shall meet the requirements of Article 700,
except as amended by Article 517.