Although the code text for 700.10(D)(1) seems to basically state the same thing in both the 2011 NEC and the 2017 NEC, the handbook commentary has made a 180 degree turn. The new commentary states the exact opposite of the 2011 commentary.
The basic rule is that certain emergency feeders need to be installed in spaces or areas that are fully protected by a fire suppression system.
In the 2011 Handbook commentary, buildings that were fully sprinklered complied with the requirement. Fully sprinklered buildings do not normally have sprinklers above suspended ceilings, since there are not usually any combustibles above the ceiling. I believe it is a standard exception in the sprinkler code. Not sure i have ever seen sprinklers above a ceiling.
According to the new 2017 Commentary, sprinklers have to be provided above the ceiling if the feeder is above the ceiling.
Why the change? Does this mean the old commentary was wrong? Are sprinklers required above the ceiling even if a building is completely sprinklered?
View attachment 2011 NEC.pdf
View attachment NEC 2017.pdf
The basic rule is that certain emergency feeders need to be installed in spaces or areas that are fully protected by a fire suppression system.
In the 2011 Handbook commentary, buildings that were fully sprinklered complied with the requirement. Fully sprinklered buildings do not normally have sprinklers above suspended ceilings, since there are not usually any combustibles above the ceiling. I believe it is a standard exception in the sprinkler code. Not sure i have ever seen sprinklers above a ceiling.
According to the new 2017 Commentary, sprinklers have to be provided above the ceiling if the feeder is above the ceiling.
Why the change? Does this mean the old commentary was wrong? Are sprinklers required above the ceiling even if a building is completely sprinklered?