David Weiszbrod
Member
- Location
- Oklahoma City
- Occupation
- Engineer
I ran across a discussion about voltage ratings on single, double and three pole breakers used in a 240V open delta service. Article 230.85 says a breaker with a 120/240 volt rating cannot be used on a 208 volt phase. It describes the rating as the limit of voltage to ground. The breaker does not connect to ground except when its a GFCI and I am excluding the GFCI in the post. While the insulated case does touch grounded parts of the panel the voltage highest potential is between the poles of two adjacent phases. In the case of a two or three pole breaker the voltage potential between the poles within the breaker is 240 volts which is greater than 208V. If it's not safe on 208v then it's not safe on 240v.
Designed insulation voltage must include current interruption voltage. Contact voltages on inductive loads can be in thousands of volts but are usually short lived. On a two or three pole the first pole to open will have 240 volts plus inductive EMF across it. The action of one pole is connected to the other pole(s) to completely disconnect the circuit.
I contend that the 120/240 means (either/or) not exclusive or. A Siemens Q120 breaker has a rating of 120/240V. Does that mean it's suitable for European panels? I yes why not US?
What are your thoughts?
David
Designed insulation voltage must include current interruption voltage. Contact voltages on inductive loads can be in thousands of volts but are usually short lived. On a two or three pole the first pole to open will have 240 volts plus inductive EMF across it. The action of one pole is connected to the other pole(s) to completely disconnect the circuit.
I contend that the 120/240 means (either/or) not exclusive or. A Siemens Q120 breaker has a rating of 120/240V. Does that mean it's suitable for European panels? I yes why not US?
What are your thoughts?
David