I am a 4th year apprentice and we are currently covering electric welders in school. My instructor gave us an example of the information on a welder name plate and told us to calculate the conductor size and overcurrent protection required. He and I came up with different answers and I believe that he may be incorrect based on the way he is interpreting the code.
As stated in 630.32 "....where the values as determined by this section do not correspond with the standard ampere rating ratings provided in 240.6 or where the rating or setting specified results in the unnecessary opening of the overcurrent device, a higher rating or setting that does not exceed the next higher standard ampere rating shall be permitted."
In the example given, the calculation for overcurrent protection did not correspond to a standard breaker size however, the next higher breaker size exceeded 300 percent of the conductor ampacity. So based on the beginning of 630.32, I interpret the verbiage to allow the use of the next higher breaker size even though 630.32(B) states that overcurrent protection cannot exceed 300 percent of conductor ampacity. He stated that you cannot round up in this scenario. His reasoning was that the opening paragraph to 630.32 only applies to 630.32(A) and not (B). This confuses me because based on the excerpt above, specifically "....where the values determined by this section....." would encompass the entire section and not just half of the section. He's been doing this a lot longer than I have but it just doesn't seem right. Perhaps someone can offer a different explanation/interpretation?
As stated in 630.32 "....where the values as determined by this section do not correspond with the standard ampere rating ratings provided in 240.6 or where the rating or setting specified results in the unnecessary opening of the overcurrent device, a higher rating or setting that does not exceed the next higher standard ampere rating shall be permitted."
In the example given, the calculation for overcurrent protection did not correspond to a standard breaker size however, the next higher breaker size exceeded 300 percent of the conductor ampacity. So based on the beginning of 630.32, I interpret the verbiage to allow the use of the next higher breaker size even though 630.32(B) states that overcurrent protection cannot exceed 300 percent of conductor ampacity. He stated that you cannot round up in this scenario. His reasoning was that the opening paragraph to 630.32 only applies to 630.32(A) and not (B). This confuses me because based on the excerpt above, specifically "....where the values determined by this section....." would encompass the entire section and not just half of the section. He's been doing this a lot longer than I have but it just doesn't seem right. Perhaps someone can offer a different explanation/interpretation?