California not to be stopped by logic and reason, has amended the 2008 NEC to add, 210.50 (E)
Originally Posted by 210.50 CEC
(E) [DPH w/ exceptions] Installation Height. The center of 15-, 20-, and 30-ampere receptacle outlets required by sections 210-
52 (A), (B), and (C) shall be installed not less than 12 inches above the floor or working platform.
Exception No.1: Receptacle outlets installed as part of permanently installed baseboard heaters are exempt.
Exception No.2: Required receptacle outlets shall be permitted in floors when adjacent to sliding panels or walls.
Exception No.3: Baseboard electrical outlets used in relocatable partitions, window walls or other electrical convenience floor outlets are not subject to the minimum height requirements.
Originally Posted by 210.50 CEC
(E) [DPH w/ exceptions] Installation Height. The center of 15-, 20-, and 30-ampere receptacle outlets required by sections 210-
52 (A), (B), and (C) shall be installed not less than 12 inches above the floor or working platform.
Exception No.1: Receptacle outlets installed as part of permanently installed baseboard heaters are exempt.
Exception No.2: Required receptacle outlets shall be permitted in floors when adjacent to sliding panels or walls.
Exception No.3: Baseboard electrical outlets used in relocatable partitions, window walls or other electrical convenience floor outlets are not subject to the minimum height requirements.