Hello all.
I have an issue with article 430, I read and read... and read and read, but I cannot find the answer to my question. I think the NEC is very clear when it comes to branch circuit conductor rating and protection against SC and GF rating, even feeder protection rating its quite clear.
But, how do you rate the conductor ampacity for the feeder?
Do you use 430.24?
Let me se if I get things right...
Say you have a feeder supplying 2 motors and lighting load.
Motor 1 = 32 FLA
Motor 2 = 5 FLA
Lload = 5 Amp
So the breaker rating would be:
80+5+5 = 90 Amp
And the feeder conductor ampacity would be:
32*1.25+5+5 = 50 Amp
That would give me a combination of a 90 Amp breaker with a 6 AWG wire, which would not be protected by the breaker.
So...
What do you do?
Am I getting this wrong?
Does the NEC requires an overload protection for the feeder? (although I can't find anything related to this matter)
Any help would be appreciated, thanks in advance .
I have an issue with article 430, I read and read... and read and read, but I cannot find the answer to my question. I think the NEC is very clear when it comes to branch circuit conductor rating and protection against SC and GF rating, even feeder protection rating its quite clear.
But, how do you rate the conductor ampacity for the feeder?
Do you use 430.24?
Let me se if I get things right...
Say you have a feeder supplying 2 motors and lighting load.
Motor 1 = 32 FLA
Motor 2 = 5 FLA
Lload = 5 Amp
So the breaker rating would be:
80+5+5 = 90 Amp
And the feeder conductor ampacity would be:
32*1.25+5+5 = 50 Amp
That would give me a combination of a 90 Amp breaker with a 6 AWG wire, which would not be protected by the breaker.
So...
What do you do?
Am I getting this wrong?
Does the NEC requires an overload protection for the feeder? (although I can't find anything related to this matter)
Any help would be appreciated, thanks in advance .